Electrical Wiring
Full house rewiring, extra circuits for heavy appliances and tidy concealed runs done in proper conduit with correctly sized cable.
View ServiceDead points, loose plugs and modular upgrades
Sockets that no longer hold a plug, switches that spark or buzz, and old boards swapped for clean modular plates.

Switches and sockets take more physical wear than any other part of an installation. Plugs go in and out thousands of times, screws loosen, contacts burn and cheap fittings crack. Most of the faults we see are small, quick and cheap to fix — and most of them get worse if they are left.
When a plug point stops working, the fitting itself is only one of the possibilities. Just as often the fault is a loose neutral in the back box, a failed connection at the previous point on the ring, or a break further back in the run.
We test rather than swap. That means checking whether voltage is reaching the box at all, whether the earth is continuous, and whether the neighbouring points on the same circuit behave normally. It takes a few extra minutes and it stops you paying for a new socket that will be just as dead as the old one.
Modular switchboards look better, but the real gain is practical: individual modules can be replaced without disturbing the rest of the plate, and the grid gives you room to add a socket or a USB module later.
When we change a board we take the opportunity to check what is behind it. Old back boxes are often shallow, crowded, and full of cable with hardened insulation. Deepening the box and re-terminating properly is what makes the new plate sit flush and last.
A three-way extension plugged into another extension behind a TV unit is a common sight and a genuinely poor idea. Each connection is a resistance, each resistance is heat, and the whole stack usually sits on a circuit never designed for it.
Where we see this we suggest putting a proper point where it is needed. In most rooms it is a short spur from an existing circuit and it costs less than people expect.
Never run a high-load appliance such as a geyser, induction hob or portable heater from an extension lead. Those need a dedicated point on an appropriately rated circuit.
Warning signs
Worn contacts no longer grip the pins. The resulting arcing generates heat inside the socket even when everything looks fine from outside.
Brown staining around a pin hole or a plate that is warm to touch means a connection is running hot. Stop using that point until it is checked.
A crackle when you operate a switch, or a visible flash, is a worn contact. In a fan regulator it can also mean the regulator itself is failing.
Questions
Most often a loose neutral or line conductor in that point or the one feeding it. It is usually a quick fix once the fault is located, and it is worth doing promptly because a loose connection generates heat.
Yes. We survey the number and size of boards first, agree a plate range with you, and normally complete a 2BHK in a day.
Yes, treat it as urgent. A tingle from a switch plate points to an earthing or insulation fault. Stop using it and call us the same day.
Either. Many customers pick a range they like and we install it; otherwise we bring good-quality standard fittings and you approve them before installation.
Related work

Full house rewiring, extra circuits for heavy appliances and tidy concealed runs done in proper conduit with correctly sized cable.
View Service
MCB, RCCB and distribution board faults traced to the actual cause — overload, earth leakage, a failed breaker or a damaged circuit.
View Service
A structured inspection of your wiring, board and earthing with a plain-language report on what is safe and what needs work.
View Service
Power gone, breaker refusing to reset or a burning smell from the board — we take emergency calls at any hour, day or night.
View ServiceFurther reading
Repairs6 min read
Switches and sockets take more physical wear than anything else in your home. Most of their faults are small, cheap and get worse if ignored.
Read article
Repairs8 min read
After enough call-outs, the same handful of problems account for most of them. Here is what they are and why they keep happening.
Read article
Safety7 min read
Most electrical safety advice is either obvious or useless. Here are the few habits that make a real difference in a real home.
Read articleSwitches & Sockets
Dead points, loose plugs and modular upgrades. Call for anything urgent, or send a WhatsApp message with your area and we will come back with a time.
Open daily · 24/7 emergency call-outs · Gaurav Path Road, Pal, Surat